tryinghard said:210.11(C)'s exception does not referance 210.23(A)
210.11(C)'s exception ONLY referances 210.23(A)(1) & (2)
Read (1) & (2) and see if lighting is stipulated as allowed with the bathroom receptacles. Read (1) & (2) and note what they DO say about lighting.
Exactly what wording is used in (1) & [or] (2) that allows lighting with the bathroom receptacles?
You don't need to reference 210.23 at all. 210.11(C) except. says if it is fed by a single 20 amp recep. outlets for other equip....
The definition of equipment will show you that lights are considered as equipment