I have encountered one of these "we always do it that way" situations.
E/C has wired many stations, but has a situation which I think is a violation.
Perhaps I am overlooking something.
To the point:
I have a conduit from a building entering gas dispenser #1 with a sealoff as my first fitting. From there, a nipple extends the run to an explosion proof Tee. From that Tee I have another conduit going back into the ground and extending to dispenser #2.
There is no sealoff in the 2nd conduit.
It seems to be a violation of 514.9.
Am I overlooking something ?
E/C has wired many stations, but has a situation which I think is a violation.
Perhaps I am overlooking something.
To the point:
I have a conduit from a building entering gas dispenser #1 with a sealoff as my first fitting. From there, a nipple extends the run to an explosion proof Tee. From that Tee I have another conduit going back into the ground and extending to dispenser #2.
There is no sealoff in the 2nd conduit.
It seems to be a violation of 514.9.
Am I overlooking something ?