N noel westphal Member Nov 15, 2006 #1 If I am interpreting 517 correctly the only wiring method to a dentist chair underground in a cement slab would be a metal conduit with a redundant ground. No way PVC would be allowed. Am i correct?
If I am interpreting 517 correctly the only wiring method to a dentist chair underground in a cement slab would be a metal conduit with a redundant ground. No way PVC would be allowed. Am i correct?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 15, 2006 #2 Yes. You would need to follow the wiring methods listed in 517.13(A).