ron
Senior Member
- Location
- New York, 40.7514,-73.9925
If this installation is deemed compliant with 645, then it supercedes the related items in Chapters 1-4.That those sections don't permit plug-in busway at all under the floor?
If this installation is deemed compliant with 645, then it supercedes the related items in Chapters 1-4.That those sections don't permit plug-in busway at all under the floor?
If this installation is deemed compliant with 645, then it supercedes the related items in Chapters 1-4.
Ron,
I thought it that way first but as you pointed out earlier, art 645 doesn't modify 300.22(C)(1) and 368.10(B)(2). Actually, it doesn't mention the busway at all. So don't they still apply?
I understand... but if the OP installation is under 2011, the slight differences could determine compliance vs violation.I quoted 2005 because thats what i'm under here and what I have for reference.
Not interconnecting cable. Interconnecting cable goes from IT unit to IT unit.If the yoked receptacle were installed at the busplug, the wiring after that point is interconnecting cable...
You have not established whether or not the underfloor space is a plenum. We do not read minds (at least I don't).Ron,
I thought it that way first but as you pointed out earlier, art 645 doesn't modify 300.22(C)(1) and 368.10(B)(2). Actually, it doesn't mention the busway at all. So don't they still apply?
You have not established whether or not the underfloor space is a plenum. We do not read minds (at least I don't).
Not interconnecting cable. Interconnecting cable goes from IT unit to IT unit.
Well that outright makes the bus plugs non-compliant.Yes...It is a plenum.
That's why I said let's stick with the appropriate NEC edition for the OP. 2008 and 2011 editions change the requirements enough to permit cord as a compliant wiring method under raised floors......
In the 2005 NEC, it's in the same paragraph (I'm sure you're well aware) "Cables other than those covered in (D)(2) ..." which goes on to list type DP in raceway or TC in cable tray ...
The demark point is where the field wiring under the NEC stops and the manufacturer supplied and listed equipment starts. NEC lists wiring methods to the outlet and cord in raceway after that point (2005). The plug and cord would have to fall under the manufacturer's equipment listing (supplied with the equipment) because it's not listed in the NEC as field wiring. Field wiring of cord to the outlet is not listed as compliant.