Cavie
Senior Member
- Location
- SW Florida
Are docks (boat lifts) included in the requirments of Art 682?
Last edited:
Cavie said:Are docks included in the requirments of Art 682?
inspector23 said:Check out Section 555.1, Scope:smile:
Cavie said:555.1 scope does not cover docks and boatlifts in single family so the question remains.
This makes no sense. If your equipment is located above the plane why would you want to shut it down at, for example, high tide?Cavie said:"Service equuipment shall disconect when the water level reaches the hight of the established electrical datum plane." Does this mean float switches and shunt trip breakers???
chris kennedy said:This makes no sense. If your equipment is located above the plane why would you want to shut it down at, for example, high tide?
I see what you mean Cavie, do you have an install your working on that would fall under 682?
M.D. that was a good read, thank you. But I see the author skipped right over Cavie's 682.11 question.M. D. said:My sympathy to you,.... this is a good article on the subject, I have no personal expierance to draw on ,..sorry.
http://www.iaei.org/subscriber/magazine/05_d/hamilton.htm
555.2 tells us to go to definitions and a dock seems to be a building"This article covers wiring, services, feeders,and grounding for floating buildings."
682.13M. D. said:Yeah it seems a little funky
From a design standpoint, the automatic disconnecting requirement will likely necessitate some sort of arrangement involving a float switch or other high water detector driving a shunt trip on the main service disconnecting means. While in theory such a system is simple and well-known, this arrangement in a waterway environment subject to silting, flooding, drifting debris impingement, etc., poses a number of design and operational challenges associated with proper location of the detector and keeping the detector clear of debris and mud to ensure proper operation. Preventing detector clogging and jamming is an issue that has been existent in high water and flood detection systems for a number of years. Choice of a detector location that is sheltered from flood-driven debris, and use of a reasonably silt-resistant detector will help reduce problems, but routine maintenance and inspection are required. Local flood control agencies can usually provide area-specific data on viable local design and maintenance/inspection strategies and equipment selection for reliability.
M. D. said:Whoops ,..I missed what it was you were commenting on ,.. sorry. They did say this in the Article , which Cavie already touched on .
http://www.iaei.org/subscriber/magaz...d/hamilton.htm