Art 708 Appication

Status
Not open for further replies.

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I?d like to get a ?sense of the forum.? We usually argue that, in absence of a specific prohibition, something that ?works? is acceptable; i.e., ?The box shall be painted? would permit any color. On the other hand, we tend to argue that if the NEC has a specific ?positive? requirement, it automatically prohibits any alternatives; ?The box shall be painted red,? shuts out all other colors. (Let?s not argue about shade, hue intensity, etc.:D)

I believe as more States adopt the 2008 NEC, my company will often be subjected to Article 708.

For the time being, I am focusing on Section 708.10(C)(1). It is my contention, the current wording would prohibit overhear pole lines for those parts of our facilities identified as COPS.

I?m not too interested in anyone?s opinion about the requirement itself, simply whether you agree or disagree that there is exclusivity.
 
I agree, with one reservation. It is not possible to protect overhead lines with conduit or concrete. None of the listed methods appear to be useable for overhead feeders, so therefore overhead is not an option.

Here is my reservation: I do not happen to know if MI cable can be used overhead. If it can, then you could use it in a COPS installation.
 