It would than be legal to run a 10/4 to the dryer and grab a 20 amp MWBC off the dryers nuetral and handle tie the two breakers?
Nope. Besides not being able to do it physically, that would place more than one circuit per phase on one conductor.

Now, if you had a dryer that did not require the neutral, you'd be okay.
 
Nope. Besides not being able to do it physically, that would place more than one circuit per phase on one conductor.

Now, if you had a dryer that did not require the neutral, you'd be okay.

My fault Larry, I am an industrial/commercial electrician that works with three phase.
 
Take the dryer for example, it utilizes a two pole MWBC and can use handle ties or a multi-pole breaker, a "two pole" breaker is not mandatory for this circuit, see 240.15(B)(2)

Roger

Doesn't the language of 210.4(C) prevent you from using handle ties in this situation? It appears to say the OCPD must open BOTH ungrounded conductors.

Nevermind... I guess EX 1 allows it for the dryer...
 
Last edited:
Can someone help me understand this article, the way it is being explained is that for every "hot" you have to have a neutral, or you can install a three pole breaker, have three hots and one neutral.

If you have a 3phase load that requires a neutral then use a 3pole breaker.

If you have 3 circuits supllying 3 seprate loads then use single pole circuit breakers

You do not have to have 3 seprate neutrals unless it is spec by the engineer..
 
Doesn't the language of 210.4(C) prevent you from using handle ties in this situation? It appears to say the OCPD must open BOTH ungrounded conductors.

Nevermind... I guess EX 1 allows it for the dryer...

210.4(B) 2011 NEC.

(B) Disconnecting Means. Each multiwire branch circuit
shall be provided with a means that will simultaneously
disconnect all ungrounded conductors at the point where
the branch circuit originates.
Informational Note: See 240.15(B) for information on the
use of single-pole circuit breakers as the disconnecting
means.
 
210.4(B) 2011 NEC.

(B) Disconnecting Means. Each multiwire branch circuit
shall be provided with a means that will simultaneously
disconnect all ungrounded conductors at the point where
the branch circuit originates.
Informational Note: See 240.15(B) for information on the
use of single-pole circuit breakers as the disconnecting
means.

So I guess in 2011 we will no longer be able to use fuses?:confused: never seen a common trip fuse:roll:
 