Article 110.15 B-Phase

Merry Christmas
Status
Not open for further replies.

l3city

Senior Member
Hi fellas,
Well according to 408.3(E) the high leg shall be marked or distinguished from the other phases when using a 120/240V, 3ph, 4-wire system. NEC 110.15 reads in part that "Such identification shall be placed at each point on the system where a connection is made if the grounded conductor is also present." Besides putting a marking/label in the panel and feeder, shall I identify each circuit breaker position (b-phase) with an orange marking or this identification will be at the point of connection whan I use the B-phase (and ground)?

Any input is welcomed, thanks ahead guys (and/or girls)

:smile:
 
shall I identify each circuit breaker position (b-phase) with an orange marking

You don't need to go that far.:smile:
 