How would the available fault current field marking be worded? My engineer has given me 14,900 AIC for my service disconnect and 15,689 AIC for the power company supply transformer , is that what should be on the field marking. I am confused about the difference between AIC and available fault current. :?
Available fault current, commonly called Short circuit Amps (SCA) is what the system can deliver.
Amps Interrupting Capacity (AIC) is what protective equipment can safely handle (this is NEC 110.9).
Short Circuit Current Rating (SCCR) is what equipment can tolerated until a protective device opens (this is 110.10).
The AIC/SCCR must always be greater than the available amount. The SCA was always pretty secret, so now the NEC wants it to be easier to find.
It is you choice, of course locl codes are applicable, as to what number you put on the label. However the numer itself will still be meaningless unless you know where it comes from.
In my opinion:
A good label would say something like; SCA = 15,689 at utility transformer dated ???. this would allow any one to recalculate things if they wanted.
Another possibility would be: SCA = 14,900 calculated at service equipment, by engineer ??? dated ???. This way we know why it is not the same as the utility.
A poor label would be handwritten a nd only say something like; 15kAIC.