This question appears on a test with four choices. The question as written is this; "Where a water pipe passes over an indoor motor control center,leak protection apparatus shall have a minimum clearance of:" A. Six feet to the protection apparatus. B. Six feet to the water pipe. C. Six and one half feet to the protection apparatus. D. Six and one half feet to the water pipe. Is it "A" "B" "C" or "D" What would be the Article # also.
 
Re: Article 110.26

rob,
i think article 110.26 (F)(1)(A) addresses this question directly. re: motor control center --indoor -- headroom above equipment -- leak protection apparatus -----answer: six feet!
 