tony_psuee
- PA/MD
I had a discussion recently with a GC regarding performance of our equipment with a field installed VFD. While discussing the installation I found out the electrician used the RMC as the EGC. That differs from the grounding instructions from the manufacturer of the VFD. I stated to the GC it appears not following the manufacturers installation instructions was most likely the problem and additionally this is a violation of Article 110.3.B. Until the VFD wiring is corrected we will not be involved on a field service basis. He stated the job passed final so he doesn't care what I think, we have an equipment problem. The EC is pleading ignorance that no one told him it required special grounding and they wired it to what they bid and Article 250 and will change it for $$$. To my knowledge that area adopted NEC2002 completely. Any feedback would be greatly appreciated.
Tony
Tony