I'll throw in my two cents worth. . .As I read it, the code describes two different minimum configurations for the Bathroom Branch Circuit.
(1) Daisy chaining the bathroom receptacle outlets of all the bathrooms on one 20 Amp bathroom branch circuit (bathroom receptacle outlets only, no lighting outlets or other outlets in spaces other than the bathrooms). This sometimes results in a long long run of cable and voltage drop concerns on the far end, but it is a NEC solution.
(2) Run as many 20 Amp bathroom branch circuits as there are bathrooms (example: 3 bathrooms = 3 20 amp circuits). One can add lighting outlets and additional load as described in 210.23 as long as these outlets and loads are in the same bathroom as the receptacle(s) served by the 20 Amp bathroom branch circuit.
210.8 says the GFI protection required is for receptacles. The notable exception, as Karen and Wayne note, is if the manufacturer requires it for their machine (I see this most commonly in the manufacturer's instructions for bath exhaust fans mounted over showers or tubs).