NEC 220.83 says the following:
220.83 Existing Dwelling Unit. This section shall be permitted
to be used to determine if the existing service or feeder is of
sufficient capacity to serve additional loads. Where the dwelling
unit is served by a 120/240-volt or 208Y/120-volt, 3-wire service,
it shall be permissible to calculate the total load in accordance
with 220.83(A) or (B).
(A) Where Additional Air-Conditioning Equipment or Electric
Space-Heating Equipment Is Not to Be Installed. The following
percentages shall be used for existing and additional new
loads.
My question is: No additional air-conditioning equipment is to be installed. So where do I include existing air conditioning loads in the calculation? It does not tell you anywhere to calculate it at 100%...