" 225.31 Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure. "
We have panel 'DP' (utility power) feeds ATS-1, from ATS-1, it feeds the load panel '1HA'. ATS-1 is also fed out of emergency source that is not part my my question.
Panel 'DP' and '1HA' locate in same building.
ATS-1 locates in a different building.
Question: Should we install one disconnect ahead of ATS and one disconnect ahead of panel '1HA' (or specify panel with main CB) before we terminate the wiring at these units so we can comply with above rule?