Can someone please clarify the intent of this Article. I know it is standard practice to run 500 MCM CU and set the OCPD at 400 Amps or parallel 500 MCM CU on an 800 Amp OCPD. With that said would it be allowed to install a # 6 THHN Cu conductor on a 70 Amp breaker because 65 Amps is not a standard size OCPD? Or is it understood to apply to larger size conductors only?