Hello,
Article 240 says that conductors shall be protected at the point where they receive their supply of power, except in 24.21(A) through (H).
24.21(B) feeder taps not more than 10 FT....
"For field installations, if the tap conductors leave the enclosure
or vault in which the tap is made, the ampacity of the
tap conductors is not less than one-tenth of the rating of
the overcurrent device protecting the feeder conductors"
what does that mean? and why this paragraph mentions the one-tenth of the rating of the feeder conductors?
Also, in general, are tap conductors protected against overload where they terminate? and protected against fault current by the OCPD that protects the tapped feeders?
I'm just confused about this one-tenth, to me a tap conductor is a a conductor whose ampacity is exceeded by the rating of the circuit upstream of the tap!!
Thank you
Article 240 says that conductors shall be protected at the point where they receive their supply of power, except in 24.21(A) through (H).
24.21(B) feeder taps not more than 10 FT....
"For field installations, if the tap conductors leave the enclosure
or vault in which the tap is made, the ampacity of the
tap conductors is not less than one-tenth of the rating of
the overcurrent device protecting the feeder conductors"
what does that mean? and why this paragraph mentions the one-tenth of the rating of the feeder conductors?
Also, in general, are tap conductors protected against overload where they terminate? and protected against fault current by the OCPD that protects the tapped feeders?
I'm just confused about this one-tenth, to me a tap conductor is a a conductor whose ampacity is exceeded by the rating of the circuit upstream of the tap!!
Thank you