dennis5150
Member
I am running four 500kcm per phase from a 800KW, 480v, 0.8pf generator (1200A gen breaker) to a switchboard (1200A main), using four 3/c 500kcm (with 3-#6 ground conductors per cable), per phase in ladder botom cable tray. According to 250.122, I need to run four 3/0 EGC's in this tray as well...or am I missing something?