Can anyone shed some light on installing parallel conductors specifically regarding the the grounded circuit conductor. Cable manufacturers make multiconductor cables with standard size configurations (for example 3-500 kcmil conductors with a #2 ground conductor). When you have (6) sets of 500 kcmil conductors (6 per phase) for ungrounded conductors, can you use multiconductor cables that only have a #2 AWG ground conductor? This has always been confusing. 2005 NEC mentioned (under 250.122 (F) (2) that you can if you have ground fault set to protect a #2 AWG conductor. 2008 NEC removed 250.122 (F) (2). Is this no longer allowed? Also, is it permitted to use the (6) paralleled #2 AWG conductors in this case as the grounded circuit conductor since these are not a minimum size of # 1/0 AWG (normally required for parallel conductors). I know that # 1/0 is not required for parallel euipment grounding conductors, but for the case when these are a feeder from a wye secondary transformer - can these (6) # 2 AWG conductors be utilized for the neutral/ground fault return path conductors?