Job info:
Residential
240 volt, Single phase
I recently did a service upgrade on a house and it failed inspection.
The inspector discussed his reason for failing the job. He referenced 250.142 b
The home had an old 100 amp service with an interior breaker panel with a 100 amp main breaker fed by a 3 conductor cable (common thing).
I removed the old meter and installed a 200 amp weatherproof panel with anMain breaker. Leaving the inside panel untouched I used the existing 3 conductor cable and connected to a 100 amp breaker in the new outside panel.
The inspector is referring to code 250.142 B as for him failing the job.
He’s explaining to me since I installed the new panel outside and turning the inside panel a sub then I must replace the 3 conductor with a 4 conductor and separate the grounds and neutrals.
I read 250.142 B
For system NOT having a main disconnecting means.
I have a 200 amp main in the outdoor panel, a 100 amp in the outdoor panel protecting the old 3 conductor feeding the old indoor panel which has a 100 amp breaker protecting that panel.
So the disconnects are there.
How do you understand this?
Should my job Pass or Fail?
Thanks Randy
Job info:
Residential
240 volt, Single phase
I recently did a service upgrade on a house and it failed inspection.
The inspector discussed his reason for failing the job. He referenced 250.142 b
The home had an old 100 amp service with an interior breaker panel with a 100 amp main breaker fed by a 3 conductor cable (common thing).
I removed the old meter and installed a 200 amp weatherproof panel with anMain breaker. Leaving the inside panel untouched I used the existing 3 conductor cable and connected to a 100 amp breaker in the new outside panel.
The inspector is referring to code 250.142 B as for him failing the job.
He’s explaining to me since I installed the new panel outside and turning the inside panel a sub then I must replace the 3 conductor with a 4 conductor and separate the grounds and neutrals.
I read 250.142 B
For system NOT having a main disconnecting means.
I have a 200 amp main in the outdoor panel, a 100 amp in the outdoor panel protecting the old 3 conductor feeding the old indoor panel which has a 100 amp breaker protecting that panel.
So the disconnects are there.
How do you understand this?
Should my job Pass or Fail?
Thanks Randy