Article 250.20 B(1)- Systems not required to be grounded?

Status
Not open for further replies.
Section 250.20 (B) states that the systems shall be grounded under the following conditions: You can read (1), (2), and (3).
 
Your not in one of those situations if this is the same system you were talking about in your other thread ( http://forums.mikeholt.com/showthread.php?t=107872&page=3 )
Not grounding a system is more uncommon then you may think, most electricians will never see a "properly installed" ungrounded system over 150v to ground in there career.

Let me re-phrase the beginning of this " you are in a situation where you need to ground the system almost always"
 
Last edited: