Well being you provide your location as NC, let's go with the 2008 NEC...
I understand that you cannot have and EGC and a bond connecting the grounded conductor to ground. My question is, do I have the option of
1) Running and EGC and not grounding my grounded conductor
or
2) Grounding my grounded conductor and omitting the EGC.
Well let's stop right here.
Under the 2008 NEC, permanently installed generators must have either a GES if a separately derived system or an EGC (stated in the requirements as an "equipment bonding jumper") sized to 250.66 or 250.122, depending on the locaiton of the OCPD.
So there is no getting around running a grounding conductor, but in the case of an SDS you'd bond your grounded conductor at the generator or at it's disconnect. In the case of a non-SDS, your grounded conductor will be solidly-connected to the service, so no other bonding grounded to grounding is permitted.
Here are some specific examples (for generators) Each generator has breaker protection.
Generator is acting as the only source and feeds multiple buildings or structures. Each building has its own Main Disconnect.
Can I bond and ground at the generator and run a EGC from each building disconnect back to the source.
Or can I bond the grounded conductor at each disconnect and use each grounded conductor as my EGC.
The generator would be an SDS, so you would bond at the generator AND run an EGC to each building's disconnect. However, there is a requirement for a GES for each building served (which maintains isolation to the grounded conductor), and a GEC requirement for the generator for building(s) served. IMO, you can run the generator GEC from a structure served in with the feeder conductors and not have to run a separate EGC. Yet, I am uncertain at this point whether you'd have to run a GEC from each structure served (I'd have to reread the req's before commenting).
Multiple generators connected to a 4 -pole transfer switch thats supplies a Main Distribution Panel.
Can I Bond at MDP only and use the grounded conductor as an EGC
No. This would be a be SDS installation in that the grounded conductor is switched.
Or Bond at each generator (don't bond at the main disconnect) and run separate EGCs
You will actually have to run GEC's
Lastly, bond and ground at both generators and the MDP using the grounded conductor as an EGC.
Any way you go about it, under the 2008 NEC, you cannot use the grounded conductor as an EGC... but again IMO, you can use the GEC's as serving a dual purpose as the EGC.
***If this were a 3-pole transfer would I bond the grounded conductor at the MDP only?
Yes.
PS: I was a bit in a hurry in typing up this response so someone please check my answers... :grin: