Bigbri0104
Member
- Location
- New Jersey
- Occupation
- Student
Hello Everyone,
On a recent installation for a two-family dwelling 200-amp service upgrade. The job we were working on was flagged. The inspector is stating I need to install a grounding wire from each service disconnect enclosure to a common grounding electrode conductor. Our state NJ is on the 2020 NEC edition. The inspector cited article 250.64 section (D) (1) saying the grounding electrode tap shall extend to the inside or each disconnecting means enclosure. I've provided a picture of the installation
The installation of the grounding electrode conductor from the ground rods and the water bond is routed through 1/2 PVC and terminates onto a ground bar that is threw bolted in the wireway. From there a properly sized jumper/bonding wire terminates from the ground bar to the grounded (neutral) conductor via Ilsco tap in the wireway. Is this installation compliant with the grounding electrode conductor and water bond? If I'm reading the charging language correctly from 250.64 (D) it states the grounding electrode connections shall be made in accordance with 250.64 (D)(1), 250.64 (D)(2) or 250.64 (D)(3). Does the OR in that statement grant permission to use any of three methods (D) (1), (D) (2) or (D) (3)? If so then this installation would be compliant with 250.64 (D) (3) option (1) grounded service conductor,
I have seen illustrations of this installation in the NEC Handbook.
My goal is to understand if I'm interpreting the code correctly.
Thanks
On a recent installation for a two-family dwelling 200-amp service upgrade. The job we were working on was flagged. The inspector is stating I need to install a grounding wire from each service disconnect enclosure to a common grounding electrode conductor. Our state NJ is on the 2020 NEC edition. The inspector cited article 250.64 section (D) (1) saying the grounding electrode tap shall extend to the inside or each disconnecting means enclosure. I've provided a picture of the installation
The installation of the grounding electrode conductor from the ground rods and the water bond is routed through 1/2 PVC and terminates onto a ground bar that is threw bolted in the wireway. From there a properly sized jumper/bonding wire terminates from the ground bar to the grounded (neutral) conductor via Ilsco tap in the wireway. Is this installation compliant with the grounding electrode conductor and water bond? If I'm reading the charging language correctly from 250.64 (D) it states the grounding electrode connections shall be made in accordance with 250.64 (D)(1), 250.64 (D)(2) or 250.64 (D)(3). Does the OR in that statement grant permission to use any of three methods (D) (1), (D) (2) or (D) (3)? If so then this installation would be compliant with 250.64 (D) (3) option (1) grounded service conductor,
I have seen illustrations of this installation in the NEC Handbook.
My goal is to understand if I'm interpreting the code correctly.
Thanks