Sorry for all the confusion LOL!!
Originally the post was regarding where the GEC was terminated. The electrical sub code official requested to install "Grounding Conductors" from each separate service disconnect. The sub code official stated, I can terminate the "Grounding Conductors" to the ground bar installed in the wireway, or tap using a "irreversible Crimp" to the GEC wire shown in the picture above from the ground rods. "Grounding Conductors" is terminology he used.
Because of the constant text message back and forth, I sent him a message stating I would add the wires. He responded back via text "Run a #4 and a #6 into each disconnect out of the metal gutter or a irreversible connector is fine." I understand possibly installing a #6 awg wire from the disconnect back into the wireway and terminating it to the ground bar. Because if any metal connection from the wireway to the service disconnect failed the #6 awg bonding wire should clear the fault connection. I'm confused on why he also wants a #4 awg too.
I installed 4# awg GEC from the copper water pipe inside, ran the wire outside where it is sleeved through the 1/2 PVC and terminated it on the ground bar inside the wireway, where it is bonded to the service neutral. The GEC from the water pipe satisfies 250.53 (D) (1) and (D) (2)
Originally the post was regarding where the GEC was terminated. The electrical sub code official requested to install "Grounding Conductors" from each separate service disconnect. The sub code official stated, I can terminate the "Grounding Conductors" to the ground bar installed in the wireway, or tap using a "irreversible Crimp" to the GEC wire shown in the picture above from the ground rods. "Grounding Conductors" is terminology he used.
Because of the constant text message back and forth, I sent him a message stating I would add the wires. He responded back via text "Run a #4 and a #6 into each disconnect out of the metal gutter or a irreversible connector is fine." I understand possibly installing a #6 awg wire from the disconnect back into the wireway and terminating it to the ground bar. Because if any metal connection from the wireway to the service disconnect failed the #6 awg bonding wire should clear the fault connection. I'm confused on why he also wants a #4 awg too.
I installed 4# awg GEC from the copper water pipe inside, ran the wire outside where it is sleeved through the 1/2 PVC and terminated it on the ground bar inside the wireway, where it is bonded to the service neutral. The GEC from the water pipe satisfies 250.53 (D) (1) and (D) (2)