Michael Park
Member
I am an Electrical contractor in Northern Virginia that needs an opinion from your forum. I have an authority that is saying that an installation is not conforming to NEC 300.3. This is the scenario. We have installed several long runs of 3/4" rigid conduit through a tunnel system. At each location of a lighting fixture or wiring device we installed a T condulet for wiring access to the fixture or device. In theses runs there are three (3) individual circuits originating from the same source sharing a neutral (grounded conductor)and ground. At the condulet, we have taken the designated phase conductor, grounded conductor, and grounding conductor out to the fixture/device and back to the condulet to continue it on to the next device/fixture. The other two phase conductors continue through the condulets until they are dropped as designated. This was done to eliminate the need for a splice in the condulet and to eliminate a potential maintenance point for the owner/maintainer. The authority has issued an opinion that this type of installation violates article 300.3. We contend that article 300.3 addresses conductors of the same circuit, and not multiphase circuits, and that if applied to the other phase conductors passing through the condulets that they are still contained in the same raceway. The authority is aying that by Article 300.3 we would have to take the other two phase conductors in and out of the device/ fixture at each location or provide a splice in the condulet. What is the opinion of the forum on this situation? Do you feel taht this is a violation of article 300.3? Thank You