Tc er cable is being used on mini splits I’ve gone to a few jobs where the cable was run by other electrician with the line set out door I assume it’s ok outdoor but indoor I see it being run next to lineset in the basement under joist
I’m reading art 336.10(9) where it should be installed with same requirements as article 334 which permits smaller than 6/2 under hoist
I’m also been told they are using it in commercial building in drop ceiling but 336.12 says not permitted except 336.10(7) so does 336.10.7 which says a threw f apply which would make it ok to put in a commercial drop ceiling
I’m reading art 336.10(9) where it should be installed with same requirements as article 334 which permits smaller than 6/2 under hoist
I’m also been told they are using it in commercial building in drop ceiling but 336.12 says not permitted except 336.10(7) so does 336.10.7 which says a threw f apply which would make it ok to put in a commercial drop ceiling