S Samuel87 Member Location Fresno CA Occupation Electrician Nov 9, 2021 #1 Hi guys I have thought to run 25’ LFMC to have power in a room in the backyard. Section 350.10 (3) says that LFMC can be used for direct burial, but they don’t say about long and deep has to be.
Hi guys I have thought to run 25’ LFMC to have power in a room in the backyard. Section 350.10 (3) says that LFMC can be used for direct burial, but they don’t say about long and deep has to be.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 10, 2021 #2 Burial depth for raceways is in T300.5. There is no limit on the length when using a wire type EGC within the LFMC.
Burial depth for raceways is in T300.5. There is no limit on the length when using a wire type EGC within the LFMC.