Article 409 (Industrial Control Panels)

Status
Not open for further replies.
There's gotta be someone out there that can tackle this!

THE SITUATION:
A particular 480V Industrial Control Panel in a "Supervised Industrial Installation" is fed from a large (say 2000 kVA) transformer, without any type of OCPD on the transformer's secondary side, and without a Main CB inside the panel. Instead, the 15-foot long "tapped" supply conductors terminate onto two separate CB's inside the control panel.

THE CODE REQUIREMENTS:
New Article 409 for the 2005 NEC requires that either a single OCPD be located ahead of an Industrial Control Panel, or a Main CB (i.e., ONE CB) be located within the Industrial Control Panel. But 409.21 states that this protection shall be provided in accordance with 240.21 Parts I, II, and IX.

THE QUESTION:
Can the reference above (to 240.21) be interpreted to mean that the Industrial Control Panel is allowed to NOT have a Main CB (Main implies ONE), nor an upstream feeder CB by satisfying one of the so-called "tap-rules" of 240.21?
 
Article 240.21 IMO addresses the conductors feeding.
Article 409 addresses within the panel
Within NEC 409 it states to use UL508A as a design guide (FPN). Under disconnects it states:
30.3.2 The disconnecting means shall open each ungrounded conductor of the supply circuit.
30.3.4 When two or more disconnects are provided for multiple supply circuits, they shall be grouped in one location on the industrial control panel.
UL is "advising" that the main OCPD reside within the Industrial Controller, rather than outside now.
Just my $.02
 