Re: Article 430.102(A) - Disconnector within Sight
Friebel,
Your quote regarding the stop start pushbutton station serving as the controller disconnecting means is not entirely accurate. If I wanted to work on the controller itself I could not isolate the load side of the start-stop contacts using the pushbutton station since 480 Volt power would still be available to the open and close contacts via the power supply from the MCC.
Given that you would not do this knowing you could go to the MCC and put the MCCB in the open position and lock it out, then go work on the controller. This is the issue I have with this article, as trained operators would never get into this situation, so I am still asking for someone show me the reason as to why this is.
[ April 05, 2004, 04:10 PM: Message edited by: wjrez ]
Friebel,
Your quote regarding the stop start pushbutton station serving as the controller disconnecting means is not entirely accurate. If I wanted to work on the controller itself I could not isolate the load side of the start-stop contacts using the pushbutton station since 480 Volt power would still be available to the open and close contacts via the power supply from the MCC.
Given that you would not do this knowing you could go to the MCC and put the MCCB in the open position and lock it out, then go work on the controller. This is the issue I have with this article, as trained operators would never get into this situation, so I am still asking for someone show me the reason as to why this is.
[ April 05, 2004, 04:10 PM: Message edited by: wjrez ]