445.13 indicates the ampacity from the generator terminals to the first distribution device containing OCPD to be not less than 115%. Since you have a set mounted breaker, IMHO, you now need to consider the circuitry from the set mounted breaker to your next piece of equipment, just a regular feeder @ the set mounted OCPD size.