This article does not cover, specifically, concealed control wiring. Just that UF, NMC copper SE.....or other cable suitable for the location.....shall be employed
This is a residential structure per the PE, but article 547 shall apply in most areas. How would you look at Cat6 and fire alarm cable concealed in wall cavity (wood studs) with a solid wood covering?
The PE wont go farther in explanation than --"comply with article 547 and use equipment listed for agricultural or industrial use". AHJ is clueless and will do whatever the PE says, but they have already confirmed copper SE and UF is acceptable.
My thought is if copper SE can be concealed in the wall, so can FPL cable and CAT cable. Not waterproof, but its all copper and water wont be getting into the walls and we are sleeving inside the wall up to 5' to prevent seepage
Regardless-
All cable below 5 feet will be in liquidtite or conduit back to their respective panels in the basement. The cable then transitions to PVC (if the device is not mounted directly to the wall surface) and all devices will be gasketed and comply with Article 503...Class III, Div II specs.
All devices shall be NEMA 4X rated (industrial IMO)
This is a residential structure per the PE, but article 547 shall apply in most areas. How would you look at Cat6 and fire alarm cable concealed in wall cavity (wood studs) with a solid wood covering?
The PE wont go farther in explanation than --"comply with article 547 and use equipment listed for agricultural or industrial use". AHJ is clueless and will do whatever the PE says, but they have already confirmed copper SE and UF is acceptable.
My thought is if copper SE can be concealed in the wall, so can FPL cable and CAT cable. Not waterproof, but its all copper and water wont be getting into the walls and we are sleeving inside the wall up to 5' to prevent seepage
Regardless-
All cable below 5 feet will be in liquidtite or conduit back to their respective panels in the basement. The cable then transitions to PVC (if the device is not mounted directly to the wall surface) and all devices will be gasketed and comply with Article 503...Class III, Div II specs.
All devices shall be NEMA 4X rated (industrial IMO)