Hi Mike, I’m huge fan and appreciate what you have done and continue to do for the trade! I have all your books lol. I have a question that I would like a little insight. Is it permissible to use a ip65 rated round high bay fixture inside a ag building? (Article 547).I now the ip65, 6 being dust and 5 being the rating for the ingress of water. So my thought is it would be. Any input would be appreciated!
 
Hi Mike, I’m huge fan and appreciate what you have done and continue to do for the trade! I have all your books lol. I have a question that I would like a little insight. Is it permissible to use a ip65 rated round high bay fixture inside a ag building? (Article 547).I now the ip65, 6 being dust and 5 being the rating for the ingress of water. So my thought is it would be. Any input would be appreciated!
Mike rarely visits the forum, so you will not get an answer from him here.

See Informative Annex F in the 2020 code for information on this issue. There is no direct crossover between Type ratings in the NEC and IP ratings from the IEC. This is one that you will need to run by YOUR AHJ.
 