Article 547
wayne t
In what code book year was underground feeders to livestock areas changed to only cooper equipment grounds not allowing aluminum any more
I'm only guessing but, I'll say 96. Thats' about the time CBS 60 minutes did a report on cows not producing enough milk due to stray voltage under power lines.
2002
2002
2002 looks like the first year with that language refering to the u/g feeder EGC running to the building.
2008: EGC within = copper 547.5(F), If livestock, EGC DB U/G = copper 547.9(D)
2002: EGC within = copper 547.5(F), If livestock, EGC DB U/G = copper 547.9(C)
1999: EGC within = copper. If u/g, then insulated or covered 547-4(f)
1996: EGC within = copper, If u/g, ins. or covered 547-8(c)
1987: EGC within = copper, If u/g, ins. or covered 547-8(c). SE = copper
1984: No mention
1987 547-8(c): Separate Equipment Grounding Conductor. In agricultural buildings as described in Sections 547-1(a) and (b), non-current carrying metal parts of equipment, raceways, and other enclosures where required to be grounded, shall be grounded by a copper equipment grounding conductor installed between the equipment and the building disconnecting means. If installed underground, the equipment grounding conductor shall be insulated or covered.