What do you think is the correct answer?
And, welcome to the zoo.... err, forum!
emoticons_spot_party.gif
 
nec 551

nec 551

the correct answer is 9 nine 50 amp 125/250v rv sites on a 200 amp 120/240 single phase service.
 
the correct answer is 9 nine 50 amp 125/250v rv sites on a 200 amp 120/240 single phase service.

9 * 50-amps = 450-amps.

Table 551.73 shows 9 sites (receptacles) may use a demand factor of 55%.

450-amps * 55% = 247.5-amp service requirement.

7*50=350*55%=192.5

7 seems to be the answer.

Did I miss something?
 
9 * 50-amps = 450-amps.

Table 551.73 shows 9 sites (receptacles) may use a demand factor of 55%.

450-amps * 55% = 247.5-amp service requirement.

7*50=350*55%=192.5

7 seems to be the answer.

Did I miss something?

551.73 Calculated Load.
(A) Basis of Calculations. Electrical services and feeders
shall be calculated on the basis of not less than 9600 voltamperes
per site equipped with 50-ampere,

9600 * 55% is 5280va per 50amp.
200a * 240v is 48000 available va
48000va / 5280va per 50amp is lil over 9 of em.
 
551.73 Calculated Load.
(A) Basis of Calculations. Electrical services and feeders
shall be calculated on the basis of not less than 9600 voltamperes
per site equipped with 50-ampere,

9600 * 55% is 5280va per 50amp.
200a * 240v is 48000 available va
48000va / 5280va per 50amp is lil over 9 of em.

Thanks, I need to slow down and read the WHOLE article I see. :D

I wish we had this in the 555 section.
 
. . . maybe a slam dunk proposal for you to put in.
Reason says you are correct; however, there has to be some documentation as to the diversity and loads to be used. The CMP will not just accept the statement that it will be the same as in 551.73. :smile:
 