The very last sentance in that video is interesting, and I think it applies to this discussion. I'm paraphrasing a little:
"If the space under the raised floor is used for air handling purposes, there is no power cord that is listed for use in an air handling space."
So if you use the underfloor space for both cooling and power cords, you can't avoid using 645.
Steve