I'm really confused with what to do here because of the code rules, I can use a suggestion or two.
The conductors going to the disconnect may be about 5 feet horizontally as if I was looking from a birds eye views according to 680.10 it has to be in rigid metal conduit.
680.12 Each means shall be readily accessible and within sight from its equipment and shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool, spa, fountain, orhot tub unless separated from the open water by a permanently installed barrier that provides a 1.5 m (5 ft) reach path or greater.
680.10 Underground wiring shall not be permitted under the pool orwithin the area extending 1.5 m (5 ft) horizontally from the inside wall of the pool unless this wiring is necessary to supply pool equipment permitted by this article. Where space limitations prevent wiring from being routed a distance 1.5 m (5 ft) or more from the pool, such wiring shall be permitted where installed in complete raceway systems of rigid metal conduit, intermediate metal conduit, or a nonmetallic raceway system.
Can non metallic raceway system be PVC?
If I win my conduit outside of the pool cage, it says nothing about the disconnect being at the bottom rather than at my waist height can you see this as a problem?
Also, it says that the disconnect has to be there but can it be on the side wall outside the pool cage separated by screen?
I would appreciate the best advise and if you can supply the code references so I can learn, I would appreciate it.


The conductors going to the disconnect may be about 5 feet horizontally as if I was looking from a birds eye views according to 680.10 it has to be in rigid metal conduit.
680.12 Each means shall be readily accessible and within sight from its equipment and shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool, spa, fountain, orhot tub unless separated from the open water by a permanently installed barrier that provides a 1.5 m (5 ft) reach path or greater.
680.10 Underground wiring shall not be permitted under the pool orwithin the area extending 1.5 m (5 ft) horizontally from the inside wall of the pool unless this wiring is necessary to supply pool equipment permitted by this article. Where space limitations prevent wiring from being routed a distance 1.5 m (5 ft) or more from the pool, such wiring shall be permitted where installed in complete raceway systems of rigid metal conduit, intermediate metal conduit, or a nonmetallic raceway system.
Can non metallic raceway system be PVC?
If I win my conduit outside of the pool cage, it says nothing about the disconnect being at the bottom rather than at my waist height can you see this as a problem?
Also, it says that the disconnect has to be there but can it be on the side wall outside the pool cage separated by screen?
I would appreciate the best advise and if you can supply the code references so I can learn, I would appreciate it.