Article 700.10 (D) Wiring, Emergency System - Fire Protection

Status
Not open for further replies.

larag

New member
NEC Section 700.10 (D)(2) Feeder-Circuit Equipment: Panelboards feeding emergency systems meet NEC fire protection requirements if they are located in a space with 2-hour fire resistance ratings (substations, electrical rooms with 2-hour fire rated walls). Assume the rooms do not have automatic fire supression system.

Question - NEC Section 700.10 (D) (1) Feeder-Circuit Wiring: Do the main feeders to these panels meet NEC fire protection requirements if these feeders are located inside these rooms with 2-hour fire rated walls, without having to concrete encase them?
 
Last edited by a moderator:
Not sure what the question is. Are you asking if there is a 2 hr. fire rated wall in the room would that satisfy the NEC?
 
Do the main feeders to these panels meet NEC fire protection requirements if these feeders are located inside these rooms with 2-hour fire rated walls, without having to concrete encase them?

If I understand your question, the answer is yes: 700.10(D)(1)(4).
 