I read through article 710 in the 2017 NEC (not a great feat, it's not even a page).
I have the following questions:
1. For 710.15(A), it states "Power supply to premises wiring systems shall be permitted to have less capacity than the calculated load. The capacity of the stand-alone supply shall be equal to or greater than the load posed by the largest single utilization equipment connected to the system." Where it says power supply or stand-alone supply, is this the ESS and the solar PV array, assuming you have both? or is this only referring to the ESS, regardless whether or not you have a PV array?
2. For 710.15(B), where it mentions 'building disconnecting means', are they referring to the back-feed breaker on the backup loads panel, assuming you are using that to interconnect the stand alone system?
and finally 3. For 710.15(D), it states "Energy storage or backup power supplies are not required." If you have no ESS, how would you have a back-up loads panel then? The solar PV array can't power that on its own without an ESS / multi-mode inverter.
Thanks again for the help!
I have the following questions:
1. For 710.15(A), it states "Power supply to premises wiring systems shall be permitted to have less capacity than the calculated load. The capacity of the stand-alone supply shall be equal to or greater than the load posed by the largest single utilization equipment connected to the system." Where it says power supply or stand-alone supply, is this the ESS and the solar PV array, assuming you have both? or is this only referring to the ESS, regardless whether or not you have a PV array?
2. For 710.15(B), where it mentions 'building disconnecting means', are they referring to the back-feed breaker on the backup loads panel, assuming you are using that to interconnect the stand alone system?
and finally 3. For 710.15(D), it states "Energy storage or backup power supplies are not required." If you have no ESS, how would you have a back-up loads panel then? The solar PV array can't power that on its own without an ESS / multi-mode inverter.
Thanks again for the help!