Is it ok to install class 2 and class 3 wiring in with 110 volt wiring (SAME device box).725.55(d)says if you have (0.25 in)separation you can.
 

bphgravity

Senior Member
Location
Florida
Re: article 725

Thats correct if you meet the requirements of that section. The two circuit types must be associated, meaning they are used for the same utilization equipment.

It may just be easier to reclassify the class 2 or 3 as permitted by the Exception No. 2 to section 725.52(A).
 