Can anyone chime in the this NYC Code requirement for fire alarm splices. To me it seems to limit unnecessary splices. In other words, if it's possible/practical for a straight run, splices must be used only when necessary.
They also have to be on labeled terminal strips.
Thoughts?
Subsection 760.130(B)(4)—Add a new subsection 760.130(B)(4) to read as follows:
(4) Terminations and Splices. Terminations and splices shall be made with terminal blocks and in listed fittings, boxes, enclosures, fire alarm devices or utilization equipment. Splices shall be limited to locations where the conditions of installation require the use of splices.
Sent from my iPhone using Tapatalk
They also have to be on labeled terminal strips.
Thoughts?
Subsection 760.130(B)(4)—Add a new subsection 760.130(B)(4) to read as follows:
(4) Terminations and Splices. Terminations and splices shall be made with terminal blocks and in listed fittings, boxes, enclosures, fire alarm devices or utilization equipment. Splices shall be limited to locations where the conditions of installation require the use of splices.
Sent from my iPhone using Tapatalk