Sounds like you need your generator neutral left floating if your transfer switch doesn’t break the neutral.I cant get this straight.. I have a (residential) 2P ATS after the main disconnect. Bonded at the main breaker and separate at the switch. Do i need to bond neutral to case at the generator or keep seperate..?
No. As in just about every other case, the EGC system is bonded to the neutral at only one point.Do i need to bond neutral to case at the generator or keep seperate..?