Bigcountry
- Gainesville, GA USA
I have a Generator that is backing up a agriculture building. My question is about the disconnect, is it required to be fused or non-fused.
The overhead 800A 120/208V service will come underground to the Disconnect which is SE rated as well. From the disc. it will feed the utility side of the ATS and the Load side of the ATS will feed into the building to a 800Amp Main Breaker Panel board.
Also the Transfer switch is not rated SE (Service Entrance) so I cannot install it without the disconnect and go straight into the ATS if that would be the answer.
Can I use this breaker as my overcurrent protection and the disconnect outside will just be our means of disconnect OR does the disconnect outside have to be fused? I would prefer the outside be fused and inside main lug but the panel is already installed with the main breaker so that is the question.
I have researched NEC 230, 240, and 702 but do not specifically see the combination of my installation. I interpret this to have to have a fused disconnect but the owner does not want to pay for it so we are trying to work this out.
Thank you for your help and may God Bless you and our Nation.
BigCountry
BigCountry