E explorer22002 Member Jul 11, 2007 #1 Is a motorized circuit breaker type automatic transfer switch allowed to be used as the main disconnecting means?
Is a motorized circuit breaker type automatic transfer switch allowed to be used as the main disconnecting means?
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Jul 11, 2007 #2 explorer22002 said: Is a motorized circuit breaker type automatic transfer switch allowed to be used as the main disconnecting means? Click to expand... We use service rated ATS's all the time. You can manually disco the service if needed.
explorer22002 said: Is a motorized circuit breaker type automatic transfer switch allowed to be used as the main disconnecting means? Click to expand... We use service rated ATS's all the time. You can manually disco the service if needed.
Jraef Moderator, OTD Staff member Location San Francisco Bay Area, CA, USA Occupation Electrical Engineer Jul 11, 2007 #3 But to be precise, your transfer switch MUST be labeled for that use, i.e. a S.U.S.E. label. But most of the ones that use breakers are labeled that way, that's the advantage of using them.
But to be precise, your transfer switch MUST be labeled for that use, i.e. a S.U.S.E. label. But most of the ones that use breakers are labeled that way, that's the advantage of using them.
E explorer22002 Member Jul 17, 2007 #4 Thanks for the info guys!! The ATS is to be fabricated based on my specs, so I'll have to make sure that it's service rated.