Let's not!!!...Let's consider the suggestion made to energize the proposed equipment from building #2...
You cannot run building #2 service-supplied power to building #1.
Let's not!!!...Let's consider the suggestion made to energize the proposed equipment from building #2...
My issue is the fact that you can manually force the outputs in the PLC to have both breakers on at the same time.I am uncertain also, but as I have read and reread it for just this case, I don't see where the means utilized is prohibited. The term transfer equipment does not directly define the equipment as being a single, integral unit.
Perhaps. I am not certain exactly how the PLC controls the breakers. What if a PLC output controlled only a relay/contactor with NC/NO circuits, mains on say N.C., and generator breakers on N.O? Under this condition it would be impossible to use the PLC to force both supplies on at the same time.My issue is the fact that you can manually force the outputs in the PLC to have both breakers on at the same time.
First thing to consider is that running feeders and branch circuits in the ducts is more dependent upon the originating power source than what building they come from or end up at. Anyway you go about it, you cannot run service-supplied-power conductors between building #1, service #1 and building #2, service #2, except under highly restrictive and special conditions.Regarding the post to consider connection to bldg #2, the question is can the existing duct bank which has feeders and branch circuits from bldg #1, be utilized to run a feeder which originates in bldg#2?
Note: The feeder will not run from bldg #2 through bldg #1 to duct bank. Rather it will run from bldg #2 to duct bank and thus share the duct bank with bldg #1 only.
Don,
The proposed equipment is a motorized gate. It is to be located at the demarcation between secure and unsecured area in an alternate access point.
As such, I assume that the installation is governed by 702.8 rather than 700.9
Consequentely, emergency and general wiring could occupy the same conduit, etc. Correct?
Thank you.
just run the gate off of the other building that has backup power.:grin:
Have you read the whole thread?
Summary (from my point of view):
Each of the two buildings has a service. IIRC, the buildings are even on separate properties but have the same owner.
You can't run normal power from the building with backup to the building that don't.
You can run backup power from the building that has it to the building that don't.
.Unless you use normal power from the building that don't have backup, you'd have to run the generator every time the gate is operated
OK... if by "Run the circuit from the building that does have backup" means a powered-by-generator-only circuit...Thats what I meant. Run the circuit from the building that does have backup. When utility power is present, the gate will run withour generator. When utility is out, the generator will run the gate.![]()
The issue is you are not providing a transfer switch for Bldg #2 to transfer power from the utility to the generator. You are trying to use a PLC for that function. 702.6
I was not clear in my statement, I also agree the section deals with transfer equipment. What I was saying is the PLC is not (as I see it) transfer equipment.
Yes, I am concerned that the utility and generator conductors may be energized at the same time.
I was not clear in my statement, I also agree the section deals with transfer equipment. What I was saying is the PLC is not (as I see it) transfer equipment.
Yes, I am concerned that the utility and generator conductors may be energized at the same time.
Transfer equipment under Article 702 only has to be approved (ref: 702.4) and not required to be labeled, listed, or otherwise required to meet any third party standard.I think the question is (the good old standby) is this PLC set up listed and approved for transfer equipment? Or is it some invention of someone who had some spare parts laying around?
I do agree with the fact that the circ. from build.2 cannot be installed in the duct bank with build.1 wireing. As was said think of some one working on the duct bank thinking every thing was dead. Or if there were a short between the wireing you then could back feed the utility.
Just go to the gate install an inverter, battery and a solar charger:grin: