sfav8r
Senior Member
- Location
- San Francisco Bay Area
I have always seen the control wires from an ATS to a GENSET run in a separate conduit. We were wiring a generator earlier today and one of the guys asked me why the control wires had to be in a separate conduit instead of running them with the feed wires since they both terminate at the same place. After thinking for a minute (I try to limit my thinking to a minute to prevent overload) it does seem that if the control wires have 600v insulation they should be able to share the conduit. I've just never seen it that way. Does anyone have a code section that addresses this? 702.9 just mentions that the standby power can share conduit with other systems. It doesn't mention the control wires. This is a non-mandatory system, but I didn't see anything in 701 either.