Let me ask the OP this. What type, brand generator are you talking about? If you are speaking of something like the residential Generac units then you would only have class I control wiring. When utility power is lost on N1 N2 it drops a relay out in the and the generator cranks. It is the voltage from the generator that energizes a relay in the ATS to do the switching. There is no back and forth "talk" between the gen. and the ATS.
Well, I agree and disagree. In the scenario you mention it would be a class 1 circuit, but often there are status lights such as battery status that are low voltage and are active during the presence of utility power. On the job that raised this question (Gilette 20Kw), there is the remote start, Battery Condition, and Charge Indicator (charging or not charging).