ATS located ajacent to panel

Status
Not open for further replies.

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
It's not service rated but it it's directly beside the panel.
By code does there need to be protection between the meter base and the ATS?
 

kwired

Electron manager
Location
NE Nebraska
If the ATS is not service rated then it needs a service disconnecting means ahead of it - which will provide overcurrent protection.

If the ATS is service rated - it is the service disconnecting means.
 