I was wondering , can you install a 200 amp ats for a whole house 22 kva on the inside of the dwelling of a single family house . there is no room on the outside next to the meter pan
Unless the ATS is not the service disconnect.Welcome to the forum.
Yes. Of course it must be service-rated, and must follow the usual "nearest point of entry" rules.
Also, in either case, the existing panel is rendered a sub-panel and must follow those rules.
True. I took it to be because he said it was to be right after the meter.Unless the ATS is not the service disconnect.