switch the grounded conductor in building 2 via the 4-pole ats. by not switching the neutral in building 2 you violate article 250.24(A)5.my point exactly,Pierre,. how do we make it code correct?
seems like its quite the dilemma..:-?
The first objective is to eliminate the parallel path between the 3 pieces of equipment, (service disconnect 1, service disconnect 2, and the generator). The main bonding jumpers in building 1 and 2 are required. Since the grounded conductor in the ats in building 1 is not switched, the grounded conductor at the generator needs to be isolated to prevent the parallel path in building 1. To keep the grounded conductor and grounding conductor seperate in building 2, a switched neutral transfer switch is required. The ground fault path, if a fault in building 1 or 2 should occur while the generator is running will travel through the main bonding jumper in building 1. There are better mouse traps to use such as two 4-pole switches or by making a 3-wire feeder in the building 2, but the are no articles preventing the use of a 3-pole and 4-pole,
Rick
Sometimes reading a post like this one is not easy for me.
Question:
Are you saying that it is permitted to make the installation with the 2 different types of transfer switches (1-3pole and 1-4 pole)?
Use two 4 pole ATS's.
I agree that the use of two 4-pole switches is a better arrangement, but can you find an article preventing the use of a 3-pole and a 4-pole switch? I can't.
I ran out of edit time, In the drawing during normal operation the neutrals are regrounded.