We have 1200a ATS. When we try to simulate power outage by turning off breaker and have generator start the breaker turns itself back on to normal power on its own. Any idea what could be happening ?
 
Yes motorized with PLC control and yes but for reason it goes back to normal and generator shuts down.

Thompson ATS
 
Yes motorized with PLC control and yes but for reason it goes back to normal and generator shuts down.

Thompson ATS
Your sensing connection is on either the load or the generator side of the switch. Could you maybe have the grid and generator connections reversed?
 