Do you have to have a seperate grounding electrode system for a subpanel when the 2 buildings are attached in the 2005 NEC. I thought that you didnt if the buillding is attached, I have been trying to find the code for it but cant.
 
Do you have to have a seperate grounding electrode system for a subpanel when the 2 buildings are attached in the 2005 NEC. I thought that you didnt if the buillding is attached, I have been trying to find the code for it but cant.
No, the feeder EGC is all that's required. If it doesn't need a main disco, it doesn't need a GEC.
 
It it really two buildings per the building codes or is it an addition to a building? If the building codes define the structures as two buildings, then it is my opinion, that 250.32 requires a grounding electrode system at each building.
 
Do the foundations connect together as one? Or are the buildings connected above ground by some sort of "breezeway" which would mean 2 buildings? ( I agree with Don):smile:
 
Do the foundations connect together as one? Or are the buildings connected above ground by some sort of "breezeway" which would mean 2 buildings? ( I agree with Don):smile:

It is possible to have the foundations connected together and still have 2 buildings. A true firewall can seperate one building into 2 buildings.

Also a "breezeway" can make 2 buildings into 1 building.

This is really a building code question.

Chris
 
It is possible to have the foundations connected together and still have 2 buildings. A true firewall can seperate one building into 2 buildings.

Also a "breezeway" can make 2 buildings into 1 building.

This is really a building code question.

Chris

This could change from one jurisdiction to another also. There are a lot of houses around my area that connect structures with breezeways and the are looked at as separate structures that need separate grounding electrodes.
 
This could change from one jurisdiction to another also. There are a lot of houses around my area that connect structures with breezeways and the are looked at as separate structures that need separate grounding electrodes.

I agree, thats why I said this is really a building code issue and an AHJ call.

Chris
 